 Post subject: IX-T7F2 hmi is rebooting itself automatcially
PostPosted: Sun Nov 01, 2015 3:37 am 

Joined: Mon Sep 17, 2012 12:38 am
Posts: 11

Offline
Dear All

I am using IX-T7F2 with schiender PLC on Modbus communication. Some time HMI is getting reboot itself automatically.

What could be the problem.

Awaiting your reply
.
Regards

Tushar


 Profile  
 
 Post subject: Re: IX-T7F2 hmi is rebooting itself automatcially
PostPosted: Tue Nov 03, 2015 7:55 am 

Joined: Mon Jun 11, 2012 2:10 pm
Posts: 89

Offline
Sadly, I've never worked with the iX-T7F2, but I have seen a similar issue on the iX-T7A.

This issue would occur due to some bug in a screen or background script. The screen would freeze for some time (while a crash report window is actually hidden behind the screen indicating a non-handled exception) and iX would reboot the panel when it discovered the program was no longer responding.

Do you have any custom script? If yes, try adding
Code:
try
{
}
catch (Exception ex)
{
MessageBox.Show(ex.Message);
}
blocks around your code to try to determine where you have a bug.

Hopefully this helps.

_________________
Adam M.
Controls Engineer
FlexEnergy


 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron