 Post subject: How to control displayed screen from PLC? [Solved]
PostPosted: Wed Sep 02, 2015 7:16 am 

Joined: Sat Jul 04, 2015 6:13 am
Posts: 25

Offline
The old Beijer e710 and e910 had a "Display Register" tag. It pointed to a PLC integer and updated the PLC with the current screen number or, if the PLC changed the value jumped to that screen number.

I have found System Tags "Current Screen Id" and "New Screen Id" but can't figure out how to tie them to the PLC.

Any ideas?


Last edited by Transistor on Thu Sep 03, 2015 1:50 pm, edited 1 time in total.

 Profile  
 
 Post subject: Re: Display register? How to control displayed screen from P
PostPosted: Thu Sep 03, 2015 1:49 pm 

Joined: Sat Jul 04, 2015 6:13 am
Posts: 25

Offline
It seems to be pretty much the same. Have the PLC write to SystemTagNewScreenId and the HMI will jump to that screen.
    The HMI only jumps on change of the tag.
    Any screens that you want to jump to must have a unique Screen ID.
    If two screens have the same Screen ID and that ID is called the HMI will reboot.
The iX Developer documentation could be a little better here.

Image

SystemTagCurrentScreenId contains the current screen ID (obviously).


 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: