Welcome Guest ( Login | Register )



All times are UTC - 7 hours [ DST ]



Post new topic Reply to topic  [ 2 posts ] 
Author Message
 Post subject: Controlling Tag source controller
PostPosted: Tue Mar 05, 2013 10:33 am 

Joined: Mon Jun 11, 2012 2:10 pm
Posts: 119

Offline
How does iX determine the source controller for a tag when multiple controllers are attached to the tag?

I have some tags sourced from a PLC that I want to send over Modbus slave connection to customer controller (two modbus slave controllers exist - one TCP, one COM). Some of these tags are read only (data direction is purely PLC>Modbus), but others are read/write and should be passed from Modbus>PLC when written to.

Finally, I have other tags that are internal tags that I would like the customer to be able to read over Modbus. Is it possible to indicate to both Modbus controllers that the tag is internal so one controller doesn't try to read it from the other?

Thanks.

_________________
Adam M.
Controls Engineer
FlexEnergy


 Profile  
 
 Post subject: Re: Controlling Tag source controller
PostPosted: Wed Mar 06, 2013 9:15 am 

Joined: Tue Mar 13, 2012 9:53 am
Posts: 824

Offline
In the tags tab in ix Developer, there is a check box called "Data Exchange", check it and it will add a Data Exchange column to the tags tab. You can then setup data exchange between controls.

The controller help tells you how to address a specific controller when multiple are defined within one controller.

For Modbus:
05:40001 addresses holding register 40001 in station 5.

iX Developer help describes how to use Data Exchange.

_________________
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer


 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC - 7 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to: