 Post subject: Intercepting the "No Communication" message
PostPosted: Thu Oct 17, 2013 9:30 am 

Joined: Fri Apr 05, 2013 1:48 pm
Posts: 15

Offline
When the HMI loses communications with the controller, we get a "No Communication" popup message.

I would like to intercept that and replace it with a screen on our HMI that lets our service personnel know what is happening and how they can test/restore communications with our controller.

How can I catch the popup and replace it with our own?

Thanks.


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Thu Oct 17, 2013 9:53 am 

Joined: Tue Mar 13, 2012 9:53 am
Posts: 824

Offline
There is no way to alter the Comm error message box. Some Controller drivers allow you to disable/enable the Comm error message box. You can check the controller driver to see if you have the option. There is a system tag which you can use that will alert you to any communication errors.

You could use the Comm error system tag to open a popup screen/dialog box by associating the screen show action with the tag. That could be done even if you cannot disable the comm error in the controller driver, you would just get the comm error and your dialog box at the same time.

_________________
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Thu Oct 17, 2013 10:18 am 

Joined: Fri Apr 05, 2013 1:48 pm
Posts: 15

Offline
Mark,

Thanks. I just found under "Tags > Controllers > Settings > Advanced > Hide Comm Error (True/False)"

If this works the way I expect, then I can turn off the system pop-up message.

Now, I'd like enable our own screen to pop-up.

How do I enable the Comm Error System tag to generate a pop-up? Do I add it to the alarms and set an action? Are there other, better ways?

I don't want to have to do this for each of our screens, I'd like this comm error action to be able to happen regardless of the screen that is being displayed.

Thanks again.


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Thu Oct 17, 2013 10:32 am 

Joined: Tue Mar 13, 2012 9:53 am
Posts: 824

Offline
As I already mentioned, you can associate actions with tags. When the comm error system tag goes higher than 0, then your action associated with the tag will fire. It does not matter what screen is open, as the action fires when the tag reaches a specific value.

Attachment:
Snap 2013-10-17 at 10.30.57.jpg
Snap 2013-10-17 at 10.30.57.jpg [ 41.96 KiB | Viewed 9178 times ]

_________________
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Thu Oct 17, 2013 12:21 pm 

Joined: Fri Apr 05, 2013 1:48 pm
Posts: 15

Offline
Perfect. I'll try it now.

Thanks


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Fri Oct 18, 2013 2:30 pm 

Joined: Fri Apr 05, 2013 1:48 pm
Posts: 15

Offline
OK - that system tag works great.

But...

What it will tell me is there is a physical loss of communication with the PLC (power off, disconnected Ethernet cable). But it does not tell me anything about the status of the program inside the PLC.

The next question:

How do I set up a watchdog so that I can monitor if the program inside the PLC is running or stopped?

The PLC can be programmed to toggle a tag on/off, but what can I do in the HMI to monitor that tag and take an action (like display a "PLC has stopped" screen) if that tag doesn't toggle after a certain amount of time?

I know I can take an action on a tag on a condition, but is there a method to monitor that condition and take an action if it doesn't change?


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Mon Oct 21, 2013 8:43 am 

Joined: Tue Mar 13, 2012 9:53 am
Posts: 824

Offline
There is no built in Watchdog functionality in iX Developer. You will have to create a program in C# to monitor the tag. You could create a timer and have the timer monitor the tag.

Pseudo code assuming a cyclical counter for the watchdog:
Timer checks value of tag and records it.
Timer checks value of tag and compares old value and current value.
If old value and new value match, PLC has stopped. If they do not, record current value.

By using a cyclical counter for the watch dog issues with how fast you poll the watchdog are eliminated.

_________________
Best Regards,
Mark Monroe

Beijer Electronics, Inc. | Applications Engineer


 Profile  
 
 Post subject: Re: Intercepting the "No Communication" message
PostPosted: Mon Oct 21, 2013 9:20 am 

Joined: Fri Apr 05, 2013 1:48 pm
Posts: 15

Offline
Thanks Mark.

That's the direction I was heading next anyway.


 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 8 posts ] 

All times are UTC - 7 hours [ DST ]


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron